#721987 - 07/17/12 05:48 PM wire size to 100 amp sub panel
Nikm Offline
Loc: L.A area Cali
Installing a new 200 amp panel and a 100 amp subpanel in attached garage. The wire run is going through the attic and is about 100 feet away. What size wire is needed for this run? thanks
#721995 - 07/17/12 07:51 PM Re: wire size to 100 amp sub panel [Re: Nikm]
Loc: Huntsville AL
I believe I used 2-2-2-4 for 100 amp at 100 ft several months ago, but wait for one of the electricians to confirm that.
#722010 - 07/18/12 01:32 AM Re: wire size to 100 amp sub panel [Re: Able_Dog]
Nikm Offline
Loc: L.A area Cali
Well I know when the run was going to be 75 feet 3 was supposedly good for it. but its now going to be about 100' the one electrician was talking about running 3 still and I am not comfortable with that if it is in the gray area. Is the '4' you included for the ground wire size?
#722139 - 07/19/12 12:34 AM Re: wire size to 100 amp sub panel [Re: Nikm]
#2 is a good choice. #3 will probably be ok, voltage drop may or may not be an issue depending on the actual load.
2-2-2-4 means three #2's and one #4.
Since your going through an attic you may need to derate the ampacity based on ambient temperature. The 90 deg. ampacity for #3 copper is 110 amps, for ambient temp. over 105 deg. F derate by .87, if over 114 deg. F derate ampacity by .82 which will come to 90.2 amps. #3 may still be code compliant since the breaker size can be rounded to the next available breaker size.