4 registered (kickintile, Able_Dog, morrisdancer, 1 invisible), 41 Guests and 1 Spider online.
#712675 - 04/11/12 11:40 AM Re: Max spaces in 100 amp panel [Re: CabinConnection]
And I think, just because I get all cynical when I'm in Chicago, that this requirement forces many panels to be replaced which could have been avoided with tandems, a further result of the "union influence" there.
Yes, good point. I think that is a reason. Some local codes here are even requiring perfectly good fuse panels to be replaced even when non-tamperable fuse size adapters are installed. When there is no valid safety reason for a requirement I figure its Chicago union influence.
#712676 - 04/11/12 12:12 PM Re: Max spaces in 100 amp panel [Re: CabinConnection]
Loc: Seneca Nation
Originally Posted By: CabinConnection
"I think some of those local requirements are to eliminate any questions as to if the panel is listed for tandems."
But I may be completely off base... wink
Nope that is a fact. smile
NYC and the big windy both have rules written by labor.
-Helen Keller
#712750 - 04/12/12 05:09 AM Re: Max spaces in 100 amp panel [Re: TJbear]
SpeedyPetey Offline
Originally Posted By: TJbear
I know there is a lot involved in figuring out load, etc, but as a rule what is the max amount of breaker spaces in a modern 100 amp setup? My current GE panel I think is from the 1980's or 1990's and has 20 spaces plus the main breaker at the top. I have two spaces left (yes, they are real spaces not fake). We had the SE cable and meter box replaced right after we moved in here but decided not to upgrade the service/panel to more than 100 amps at the time. Sorta wishing we had, lol. A few more spaces would be golden. Its a tiny house but I did a lot of work rewiring, regrouping, and separating things to bring it up to modern code so I used up most of the spaces. Be nice if we could get a slightly larger panel with the current feed.......
A few panel makers have 32 space 100A MB panels. I know SqD QO does for sure. I just used one recently.
Signature starts here:
#712799 - 04/12/12 09:46 AM Re: Max spaces in 100 amp panel [Re: SpeedyPetey]
TJbear Offline
Loc: WNY
Wow, never would have guessed 100 amps can support 32+ breakers. I guess you'd have to be careful not to overload it, though.
I'd say the biggest loads in my house would be the fridge, 10k BTU window A/C unit (on its own 20 amp circuit) and occasional space heater usage. The range, hot water tank, clothes dryer and furnace are gas. Not really much load in the house but I was planning on using the 50 amp breaker from the old range feed to feed a 50 amp sub panel in the detached garage at some point.
I also may have some drain tile work and a sump pit installed (ugh!) at some point so there's another 20 amp breaker. That will leave me with one space left. Not sure I want to jam a bunch of those slim breakers in, it's already sorta crowded in there (if it can even accept them, haven't been able to determine yet. Nothing mentioned about it on the sticker).
Might be worth it to upgrade to a larger panel and/or service when/if I do the garage project......?
Maybe I'll type up my current circuits and what they feed and post it.
#712800 - 04/12/12 09:50 AM Re: Max spaces in 100 amp panel [Re: TJbear]
Its not about the # of circuits. Loads are calculated according to the code using the load calculation rules. For example lighting/general receptacles is calculated at 3VA per square foot. The # of breakers and the amperages of breakers means nothing for load calculation purposes.
#712801 - 04/12/12 09:53 AM Re: Max spaces in 100 amp panel [Re: MCA]
TJbear Offline
Loc: WNY
So listing my circuits won't really tell you anything? The house is about 900 sq feet.
#712802 - 04/12/12 10:12 AM Re: Max spaces in 100 amp panel [Re: TJbear]
NEC load calculations for a dwelling unit are to allow 3VA per square foot. Also allow 1,500VA for each kitchen appliance and laundry circuit (yes, they can handle 2,400VA but the assumption is they will not all be loaded up to capacity at the same time). Add the larger of the heating or air cond. load. Then add any major appliances using their load. And even at that there are demand factors for some loads that can reduce the value.
So the listing of circuits with appliance ratings is part of the load calculation, just not for lighting circuits (lighting and receptacles in bedrooms, living rooms, etc.)
Edited by MCA (04/12/12 10:13 AM)
#712837 - 04/12/12 01:10 PM Re: Max spaces in 100 amp panel [Re: TJbear]
With the newest code rules and dedicated circuits(kitchens, bathrooms, laundry etc) the count goes up a lot from back when the panel was first installed.