#654130 - 03/04/11 08:10 AM zinsco gfi 15A
thumped Offline
newbie

Registered: 03/03/11
Posts: 10
I have a Zinsco 15 A gfi that the test button doesnt work on. Can I leave the gfi in my panel box and change out the outlets to which it feeds with individual gfi's? Should I put in a regular breaker instead? Do I need to change the wiring if changing the breaker to a regular one? Thanks for any help.

Top
#654131 - 03/04/11 08:46 AM Re: zinsco gfi 15A [Re: thumped]
MCA Offline
Carpal Tunnel

Registered: 03/09/06
Posts: 4532
Loc: Illinois
The test button tests the GFCI sensing device, which failed. The breaker should still be providing over current protection. Besides confusion, I can't see why it has to be replaced if you use GFCI receptacles. Zinsco is an obsolete brand (with some reported troubles), replacements may be hard to find. In the future you may want to consider a new panel.
Its a single pole GFCI, right? If its a double pole feeding split receptacles there will be some issues replacing receptacles.
You can put in GFCI receptacles. One GFCI at the first in the line can protect the rest of the circuit if wired to do so.
What does the circuit feed? Was the GFCI used to compensate for lack of grounding (as allowed for old houses)? If so you want probably want GFCI protection on the whole circuit.


If you replace the GFCI breaker with a regular one you need to remove the neutral connection at the GFCI breaker and connect it directly to the neutral bus bar.


Edit...added comments
If you leave the non-working GFCI breaker leave a note at that breaker indicating that the GFCI portion is not working and GFCI protection is provided by GFCI receptacles to avoid any confusion or false of safety (so no one thinks the whole circuit is protected if it is not).


Edited by MCA (03/04/11 11:31 AM)

Top
#654132 - 03/04/11 12:57 PM Re: zinsco gfi 15A [Re: MCA]
thumped Offline
newbie

Registered: 03/03/11
Posts: 10
You are correct, it is a single pole gfci. I want to leave the breaker as is and install a gcfi at each recepticle that it feeds which are the bathroom outlets and the outside outlets on the house. I just didnt know if I needed to change out the circuit breaker or not without doing any extra wiring. All the house recepticles are grounded. Thanks for you help, its very much appreciated.

Top
#654133 - 03/04/11 03:07 PM Re: zinsco gfi 15A [Re: thumped]
Gizmologist09 Offline
Handyman

Registered: 02/08/09
Posts: 606
Loc: Palmdale, California USA
Zinsco? UH-OH!

Top
#654134 - 03/04/11 07:42 PM Re: zinsco gfi 15A [Re: Gizmologist09]
bacp Offline
enthusiast

Registered: 10/13/03
Posts: 211
I`m wth GIZ. When did these bums get back in business.

Top
#654135 - 03/04/11 07:46 PM Re: zinsco gfi 15A [Re: bacp]
Punky Offline
Carpal Tunnel

Registered: 06/01/05
Posts: 3145
Loc: Springville, NY
_________________________
Bupkis mit Kuduchas!
Opinions should be verified with your local town Board/Inspector/Review Panels

Top
#654136 - 03/05/11 07:04 PM Re: zinsco gfi 15A [Re: Punky]
bacp Offline
enthusiast

Registered: 10/13/03
Posts: 211
Punky; I cant believe it. Obviously going to attempt to make a poor product worse.

Top
#654137 - 03/06/11 07:36 AM Re: zinsco gfi 15A [Re: bacp]
Punky Offline
Carpal Tunnel

Registered: 06/01/05
Posts: 3145
Loc: Springville, NY
Ya, I know. Here's the part I like:

"The use of manufactures registered trademarks herein is for identification purposes, and educative value only, as commonly denoted in the trade. JRL Electric Supply, Inc. is not an authorized distributor of Zinsco distribution and control products. All trademarks herein are, and remain the proprietary interests of the manufacturer as credited."

I guess the "educated value" translates as, "oops, we burned down your house. Hope you learned not to use Zinsco breakers!" And they're not authorized to distribute a crappy product.
_________________________
Bupkis mit Kuduchas!
Opinions should be verified with your local town Board/Inspector/Review Panels

Top
#654138 - 03/06/11 10:26 PM Re: zinsco gfi 15A [Re: Punky]
MCA Offline
Carpal Tunnel

Registered: 03/09/06
Posts: 4532
Loc: Illinois
I didn't think Zinsco is made anymore, the Zinsco breakers are probably made by a generic manufacturer for replacement use. Just like Federal Pacific repalcement breakers are made, but not made by Federal Pacific.
I have never worked inside a Zinsco panel before, they don't seem to be that common in my area, although I seen my fare share of Federal Pacific panels.

Top
#654139 - 03/09/11 07:37 PM Re: zinsco gfi 15A [Re: MCA]
bacp Offline
enthusiast

Registered: 10/13/03
Posts: 211
MCA: lucky you for not having to work inside a Zinsco panel. Home of molten bus bars and welded in circuit breakers.

Top